4.1 PIPELINE DIAMETER
Inlet water :
EUROKONUS 3/4
Outlet water :
EUROKONUS 3/4
Condensate discharge : Ø 14 mm (internal diameter)
For the position of the pipeline and the wall fixings, refer to the
designs shown in the following sections, based on the specific
configuration.
4.2 CONNECTIONS
The choice and sizing of the hydraulic lines must be made by
an expert who must operate according to the rules of good
technique and the laws in force.
Insulate the water lines / In the figure are indicated the optional components
4.3 CONDENSATION DISCHARGE
The condensation discharge network must be suitably sized
(minimum inside pipe diameter 14 mm) and the pipeline
positioned so that it keeps a constant inclination, never less
than 1%.
In the vertical installation, the discharge pipe is connected
directly to the discharge tray, positioned at the bottom of
the side shoulder underneath the hydraulic fixtures.
In a horizontal installation the discharge tube is connected
to the one already present on the machine.
If possible, make the condensation liquid flow directly in a
gutter or a "rainwater" discharge.
When discharging directly into the main drains, it is advisable
to make a siphon to prevent bad smells returning up the pipe
towards the room. The curve of the siphon must be lower
than the condensation collection bowl.
If the condensation needs to be discharged into a container, it
must be open to the atmosphere and the tube must not be
immerged in water to avoid problems of adhesiveness and

4 - WATER CONNECTIONS

To make the connections:
position the hydraulic lines ( ref. A)
tighten the connections using the "spanner and counter
spanner" method ( ref. B)
check for any leaks of liquid
coat the connections with insulating material ( ref. C).
The hydraulic lines and joints must be thermally insulated.
Avoid partially insulating the pipes.
Do not over-tighten to avoid damaging the insulation.
Use hemp and green paste to seal the threaded connections;
the use of Teflon is advised when there is anti-freeze in the
hydraulic circuit.
counter-pressure that would interfere with the normal outflow.
However, on completion of the installation it is advisable to
check the correct outflow of the condensation liquid by slowly
pouring about ½ l of water into the collection tray in about 5-
10 minutes.
If there is a height difference that could interfere with the
outflow of the condensation, a pump must be mounted
(provided by the customer)