Herunterladen Inhalt Inhalt Diese Seite drucken

Plug Assignment - SICK T4000 Bedienungsanleitung

Direct unicode safety switch
Vorschau ausblenden Andere Handbücher für T4000:
Inhaltsverzeichnis

Werbung

Verfügbare Sprachen
  • DE

Verfügbare Sprachen

  • DEUTSCH, seite 1
Operating Instructions
T4000 Direct Unicode
Fig. 6: Plug
assignment
Tab. 3: Plug
assignment
© SICK AG • Industrial Safety Systems • Germany • Subject to change without notice • 8012206/UC32/2010-11-15
Electrical connection
All relevant values can be determined using Tab. 2:
 Select the corresponding section in the n column (max.
number of switches), here: 6 switches
 In the i
column (possible output current per channel
OUT
OA/OB) find a current greater/equal to 75 mA, here
100 mA.
 The maximum cable length to the first switch can be
taken from the L
Result: The required cable length L
allowed in the table at 40 m. The total length of the chain
of switches L
is, at 140 m, within the maximum value of
max
200 m. The planned application is feasible in this form.
5.5

Plug assignment

RST
UB
0 V
IA
IB
OA
OB
OUT
Pin
Designa
tion
1
IB
2
UB
3
OA
4
OB
5
OUT
6
IA
7
0 V
8
RST
column, here 50 m.
1
1
8
2
7
6
1
3
4
5
Description
Enable input for channel 1
Power supply 24 V DC
Safety output channel 1
Safety output channel 2
Signal output
Enable input for channel 2
Weight, 0 V DC
Reset input for hardware reset
Chapter
is within the values
6
7
8
1
2
Wire colour
white
brown
green
yellow
grey
pink
blue
red
5
5
4
3
157

Werbung

Inhaltsverzeichnis
loading

Inhaltsverzeichnis