Installation
1
Must be installed by a competent person. To ensure
your safety, make sure the mains power is switched OFF
before accessing wiring.
1.1
Guidelines
1.2-1.5m
1.4
Configure the Thermostat
The switches are located on the back of the faceplate. Default settings are highlighted.
Switch
Description
Cycles (proportional)
1 & 2
Span (conventional)
3
Clock display
4
Temperature display
1
5
Temperature control mode
6
Pump protection
2
1. If you change from °C to °F (or vice versa), you will need to reprogram your Comfort, Economy and Vacation settings.
2. For hot water installations, it is recommended to enable this option to activate the pump for one minute every
24 hours to prevent pump seizure.
1.4.1
Proportional Adaptive Mode (switch #5)
This mode analyzes previous cycles to define the the next duty cycle. This control mode guarantees optimal
temperature control based on the system's capacity. To extend the life of the system, a minimum On/Off time
of 10% of the cycle has been implemented.
Ideal for:
• Radiant or convection electrical heating system
• Circulator control in a hot water system
• Electrical hot-air furnace
• Conventional gas or fuel hot-air furnace
Heating Cycle Selection (switches #1 and #2)
Select the cycle using switches #1 and #2. Short cycles help eliminate temperature variations,
thus increasing user comfort.
1.5
Install the Batteries
When you first install the batteries, the unit runs a sequence of tests and a complete reset to zero.
J
The screen should display 0:00 MO
and the ambient temperature. The current setpoint is 20°C.
1.5.1 Replacing the batteries
The thermostat will display an icon indicating that the batteries must be replaced. This icon
will be displayed for 60 days; after this delay, the thermostat will shut down the heating unit.
The time and programming are saved for 15 seconds when replacing the batteries.
Basic Configuration
2
2.1
Set the Time and Day
1
Set the time, using the Hour and Minute buttons.
2
Set the day, using the Day button.
2.2
Configure the Setpoints
2.2.1
Comfort and Economy
These setpoints are associated to the schedule's programs and are pre-programmed as follows:
R
Comfort
20°C (68°F)
ƒ
Economy
18°C (64°F)
2.2.2
Vacation
This pre-programmed setpoint is used when the Vacation mode is activated.
Vacation
10°C (50°F)
Program Your Schedule
4
The thermostat allows four setting changes for each day of the week. There are no pre-set programs. Your
heating system switches betwwen the Comfort setpoint and the Economy setpoint according to the times you
would have set.
Programs
Associated Setpoint
PROG 1
PROG 2
PROG 3
PROG 4
4.1
Set or Modify the Programs
1
Press Program. The screen displays MO and PROG 1.
2
Press Day to select the day (hold for 3 seconds to select all days of the week).
3
Press Hour and Minute to set the start time. To clear an entry, press Clear, the time zone displays --:-- when
the program is inactive.
4
Press Program to select the program number (2, 3 or 4).
5
Repeat steps 3 and 4 for remaining programs.
6
Press Manual/Auto to exit.
To erase program for desired day:
1
Press Program until desired program is selected.
2
Press Day to select desired day.
3
Press Clear to erase the time (--:--).
4
Press Manual/Auto to exit.
EN + DE
1
2
3
4
6
7
8
UP
DOWN
15 min (see 1.4.1)
0.5°C (0.9°F) (see 1.4.2)
12H
24H
°F
°C
Proportional (see 1.4.1)
Conventional (see 1.4.2)
Deactivate
Activate
Programs 1 and 3
Programs 2 and 4
Time
R
Wake-up
(Comfort)
ƒ
(Economy)
Leave
R
Return
(Comfort)
ƒ
Sleep
(Economy)
1
Loosen the captive screw holding the faceplate to the mounting plate.
2
Pull the lower part of the faceplate to remove it from the mounting plate.
3
Loosen the screw (captive) holding the wire cover and remove the wire cover.
4
Pull wires through the hole in the mounting plate and secure the mounting plate to the wall
(or onto an electrical box for line voltage wiring) using the enclosed wall anchors and screws.
5
Wire the thermostat to the heating system and, if necessary, connect the remote input.
6
Once wiring is complete, re-install the wire cover.
7
Use the switches located at the back of the faceplate to configure your thermostat according to your application.
8
Install the batteries.
9
Mount the faceplate on the mounting plate and tighten the screw.
1.2
Thermostat Wiring
For a 2-wire connection: no polarity.
Direct wiring to the circulator
5
Connection to the thermostat terminals of a furnace
Relay
9
For a 3-wire connection: observe the polarity
Wiring to a power-operated mixing control valve
Cycles
5 minutes
10 minutes
15 minutes
20 minutes
1.4.2
Conventional mode with anticipation (switch #5)
This mode is compatible with all heating systems.
Programmable Span Selection (switches #1 and #2)
Select the span using switches #1 and #2. The default temperature span is 0.5°C. For example, if the
temperature setpoint is 20°C, the heating system will turn on at 19.5°C and turn off at 20.5°C.
Span
0,3°C
0,4°C
0,5°C
0,6°C
2.2.3
To Modify a Setpoint
1
Set the temperature using pq.
2
Press and hold one of the setpoint buttons (
on the screen (approx. 3 seconds).
2.3
View the Current Setpoint
To view the current setpoint, quickly press once one of the arrow buttons pq.
The screen displays the setpoint; the arrow indicates a setpoint.
Select the Operating Mode
3
3.1
Automatic
This mode executes the schedule. To activate:
• Press Manual/Auto until
3.1.1
Temporary Bypass
When in Automatic mode, you can temporarily bypass the current program setpoint until
the beginning of the next program. To bypass:
• Set the desired temperature pq OR quickly press
3.2
Manual
This mode allows you to maintain a constant temperature.
• Press Manual/Auto until is displayed.
• Set temperature pq OR quickly press
3.3
Vacation
Maintains a specific temperature when away for a prolonged absence (e.g. vacation).
• From the thermostat, quickly press to activate.
Technical Specifications
5
Power supply: 2 AA or LR6 alkaline batteries 1.5 V
Max. resistive load: 5 A @ 240 VAC / 5 A @ 30 VDC
Max. inductive load: 2 A @ 240 VAC / 2 A @ 30 VDC (P.F. = 0.4)
Remote input: 12 VDC, ± 10%, 2.5 mA
Certifications: CE, c UL us
Control device: Electronic
Automatic action: Type 1 B
Number of programs: 4 programs / day, total of 28 programs
Storage temperature: -20°C to 50°C (-4°F to 122°F)
Operating temperature: 0°C to 50°C (32°F to 122°F), 95% R.H.
Temperature setting range: 5°C to 30°C (40°F to 85°F)
Temperature display resolution: 0.1 degree
Temperature reading accuracy: ± 0.5°C (± 0.9°F)
Software: Class A
Protection class: II
Protection degree: IP 40
The terminals are designed to handle a cross-section of wire measuring up to 2.5 mm2 (14 AWG).
Bk-electronic GmbH
Hardhofweg 40
74821 Mosbach
Germany
For assistance with this product please visit
livewell.honeywellhome.com
1.3
Remote Input Wiring
The thermostat is equipped with a remote input
which allows connection of a telephone controller or
a home automation system. When a signal is received
through this input, the thermostat will automatically
240 V
switch from normal operating mode to Vacation
mode. For details on operating the telephone
controller, refer to the instruction manual.
Connection to telephone controller
or a home automation system
Furnace
T140
240 V
EUROPE
Not recommended for furnaces
Gas or electric wall furnace
Fuel or gas floor furnace, forced air heating
Commercial unit
Hot Water Heating
Forced Air Heating
Not recommended
Not recommended for
for furnaces
central units
Radiant or convection
Gas or electric wall furnace
electric heating
Fuel or gas floor furnace,
Central heating
forced air heating
Commercial unit
R
or
ƒ
or
) until the icon is displayed
is displayed. The program setpoint icon is displayed.
R
or
ƒ
to use a pre-defined setpoint.
J
R
ƒ
or
to use a pre-defined setpoint.
© 2019 Resideo Technologies, Inc.
This product manufactured by Resideo and its affiliates.
The Honeywell Home trademark is used under license
from Honeywell International Inc. All rights reserved.
33-00057ED-02
Home automation system
or telephone controller
Position
Position

Werbung

loading

Inhaltszusammenfassung für Honeywell Home Resideo T140

  • Seite 1 This product manufactured by Resideo and its affiliates. Press Day to select desired day. For assistance with this product please visit The Honeywell Home trademark is used under license Press Clear to erase the time (--:--). livewell.honeywellhome.com from Honeywell International Inc. All rights reserved.
  • Seite 2: Installation

    Drücken Sie so lange auf „Program“ [Programm], bis das gewünschte Programm ausgewählt ist. Weitere Informationen zu diesem Produkt Die Marke Honeywell Home wird unter der Lizenz von finden Sie auf der Website von Drücken Sie auf „Day“ [Tag], um den gewünschten Tag auszuwählen.
  • Seite 3 This product manufactured by Resideo and its affiliates. Pour de l’aide, visitez notre page internet Appuyer sur Day pour choisir le jour souhaité. The Honeywell Home trademark is used under license livewell.honeywellhome.com Appuyer sur Clear pour effacer l’heure (-:-). from Honeywell International Inc. All rights reserved.
  • Seite 4 Druk op Programma totdat het gewenste programma is geselecteerd. dochterondernemingen. Druk op Dag om de gewenste dag te selecteren. Het Honeywell Home-handelsmerk wordt gebruikt Ga voor hulp bij dit product naar onder licentie van Honeywell International Inc. Druk op Wissen om de tijd te wissen (--:--).
  • Seite 5: Instalación

    Pulse Program hasta que aparezca el programa deseado. This product manufactured by Resideo and its affiliates. Para asistencia sobre este producto visite The Honeywell Home trademark is used under license Pulse Day para seleccionar el día. livewell.honeywellhome.com from Honeywell International Inc. All rights reserved.
  • Seite 6: Dati Tecnici

    Cancellazione del programma per un determinato giorno: Prodotto realizzato da Resideo e sue affiliate. Il marchio commerciale Honeywell Home viene Premere il pulsante di regolazione del programma fino a selezionare il programma desiderato. Per assistenza su questo prodotto, accedere al utilizzato su licenza di Honeywell International Inc.
  • Seite 7 Vymazání programu v určitém dni: Germany přidruženými společnostmi. Držte stisknuté Program, dokud není vybrán požadovaný program. Ochranná známka Honeywell Home je používána na Pokud potřebujete pomoc s tímto produktem, Stiskněte Day a vyberte den. základě licence od společnosti Honeywell International navštivte web livewell.honeywellhome.com...
  • Seite 8 Nemecko Tento produkt vyrába spoločnosť Resideo a jej pobočky. Stláčajte možnosť Program, až kým nie je vybraný požadovaný program. Ochranná známka Honeywell Home sa používa Stlačte možnosť Day a vyberte požadovaný deň. Ak potrebujete pre tento produkt pomoc, na základe licencie od spoločnosti Honeywell Stlačte Clear, ak chcete vymazať...
  • Seite 9 W celu usunięcia programu dla danego dnia: jej spółki powiązane. Naciśnij opcję Program, aż pojawi się wymagany program. Znak handlowy Honeywell Home jest używany na Informacje na temat tego produktu znajdują Naciśnij opcję Dzień, aby wybrać wymagany dzień. licencji firmy Honeywell International Inc.Wszystkie się...
  • Seite 10: M Szaki Adatok

    Ezt a terméket a Resideo vállalat és leányvállalatai Nyomja meg a Program gombot, és válassza ki a kívánt programot. látogasson el a livewell.honeywellhome.com gyártották. A Honeywell Home védjegy a Honeywell Nyomja meg a Nap gombot a kívánt nap kiválasztásához. weboldalra International Inc.